Hi all,
So here the situation, was doing some testing today in advance of board change tomorrow (domestic).
Currentl board has one 'socket' circuit. There are however 2 rings going into the one breaker.
So seperated the two rings and found one just does a small office that was built as extension on back of garage (right next to board).

Test resulst as follows for this ring (2.5mm T&E):
End to end
L-L 0.08
N-N 0.08
E-E 0.19

Now when i cross connect and test L-N & L-E these are results I get at the 5 sockets on the circuit.

L-N 1.11, .67, .07, .07, .06
L-E 1.2, .4, .08, .08, .08

Any ideas what could be going on? IR is all >299MO

Based on end to end tests i was expecting approx 0.04 for L-N and 0.06 for L-E, these two sockets seem to be giving odd readings?

Have had them off and all connections tight.

Any help much appreciated. Sorry for the babbling.
 
are you testing using a breakout box or at the connection terminals?? Sometimes plug in test equipment can give strange results.
 
could be poor connections IN sockets, or some might be spurs. pick one of the high reading sockets and test at the cables ( bit of a pain , but could give better result.)
 
Maybe your leads, I had some crazy readings before I realised that the cores had parted company.
 
Last edited by a moderator:
Thanks guys, some good things for me to try tomorrow. Interesting what you say about the leads, i have noticed them becoming a bit unsteady!
 
Just a quick update guys, changed batteries on tester and bingo! Megger 1553, thanks for advice all.
Glad you sorted it...I always keep a spare set in the van now just in case.... every time you first turn it on to 'V' it will come up with your battery level you have left mines around 10.7v..... keep an eye on that think when it gets around 8v it goes a bit funny:freak:

Sy
 

Reply to Odd results on a ring!?! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
855
  • Question
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
    • Like
    • Winner
Replies
0
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top