Evening gents, I'm sure I'll get shot down for being stupid or missing the obvious , but here goes anyway.
TT supply to wooden building, Ze 88 ohms. (bonding disconnected). only service is water coming in in a poly pipe.
Zs on
one RCD between 0.5 and 1.5. on the other rcd between2 and 3. Got the same results with bonding to little bit of copper pipe on or off. R1 R2 all as expected.
Can,t figure out why Zs different on each rcd by the same amounts and why Zs so much better than Ze.
Hope I've explained it ok. Any answers appreciated.Any abuse will make me sad.
Regards,
Martin.
 
Have you IR tested?....could be a N-E fault on one of the circuits,which dont always trip RCD's on TT systems and will bring down your Zs readings as effectively the N and earth are joined.
 
Have you IR tested?....could be a N-E fault on one of the circuits,which dont always trip RCD's on TT systems and will bring down your Zs readings as effectively the N and earth are joined.
Bang on that man. Re did IRs, builder found some more nails and got cable twice on skirtings.
Suppose 'there's a lesson there.
Owe you a pint.
Martin.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Odd Zs s
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
baggy61,
Last reply from
baggy61,
Replies
4
Views
1,022

Advert

Back
Top