Official safe isolation procedure | on ElectriciansForums
Discuss Official safe isolation procedure in the Electrical Course Trainees Only area at ElectriciansForums.net
gazdkw82
leicester
I'm making some flash cards for revision and I'm doing a flash card on the safe isolation procedure.
can you tell me if this is correct
1. Seek permission to isolate and carry out work
2. locate and identify known sources of supply
3. Identify means of isolation
4. Isolate, remove fuse/lock off isolation switch or circuit breaker
5. Secure isolation
6. Fit warning notice
7. Selector approved voltage indicator with leads compliant to gs38
8. Verify voltage indicator with known supply or proving unit
9. Test between all lines, all L-L, all L-N, all L-E, all N-E
10. Retest voltage indicator with known supply or proving unit
thanks
If the means of isolation is not suitable for disconnecting under load, then switch off the load(s) (between 3 and 4).
5. Secure isolation
thanks
file:///C:/Users/Pete/Downloads/Best-Practice-Guide-2(2).pdf hope you can see this PDF
Here's Elecsa's freely downloadable pocket guide to isolation. There's a tonne more pocket guides (33 I think) you can download covering various topics.
  • Pocket-Guide-5 - Isolation.pdf
That's the one I was trying to send, see nothing wrong with a bit of IT experience lol.
Reply to Official safe isolation procedure in the Electrical Course Trainees Only area at ElectriciansForums.net
View: https://www.youtube.com/watch?v=glsg2HpWyok
Hi all. OK... Let me just try and clear a 1" square space on the screen inbetween all the highly intrusive ads.... On a site (NHS in fact) and...