Hi folks, pick your brains a wee bit here. Was looking at a converted Rayburn for someone today, the thing keeps locking out every so often. It's run of a programmer to a Danfoss controller onto the burner & oil pump etc. After a bit of investigating someone told me there's a good chance it could be the photocell needs wiped or replaced. After locating it & giving it a wipe I tried again & nothing, was locking out again. I held the button on the controller as this gives you a signal using the lights to describe the fault, the light flashed three times which I was informed means it's a photocell fault. Now I'm waiting on a photocell to come home I ordered but tonight whenever the there is power coming from the programmer to the controller everything is fine until you press the controller start, it's tripping the RCD. Is there anything else I should be looking at or do you think the photocell is causing this now? Apparently it's been cutting out for the last 2 weeks every 3-4 hours but tonight is the first it's tripped the RCD. To be honest the burner etc is over 10 years old so it could be on it's way out! I've never worked internally on one of these things before, just having a look as a favour but I'm keen to know a bit more & maybe pick up some info for this one obviously & for future incase I come across this again. Any help would be much appreciated.
 
Check the coil on the oil solenoid valve, A mate of mine had a similar fault on his oil fired Stanley range that numerous burner engineers had looked at over 18 months or so I was staying over when it started playing up for the final time and the burner would not stay on and sometimes would not fire at all swapped the solenoid valve coil over from the cooker burner onto the heating burner and got it working. Did an IR test on the suspect / faulty coil and was getting a very low reading to earth replaced the coil and the problem was solved

Just looking at the info in your post is the burner actually firing and then locks out because the photocell is not detecting the flame or is the burner not firing at all and the photocell because it is not seeing a flame then locks the burner out
 
As above,check the solenoid,I went out to one and the guy had replaced every part on the burner except the solenoid and it was actually that which had gone.

Sounds like it might be the same guy or one that went to the same training school that went to my mate's house changed more or less everything except the solenoid and that was the faulty part
 
In the factory where I once worked there where oil fired space heaters which I think were called Dravoes.


To test the photocell a DC µA meter was connected in series with the photocell and the control unit.


If my memory serve me right a small DC current will flow when the flame is sensed.


The value of this reading is set by the type of control box, I think the readings were:


No Flame/Dark ≤5µA
Flame/Light ≥65µA.


Hope this helps.
 

Reply to Oil burner photo cell in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
111
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
810
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
814

Similar threads

Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of...
2 3
Replies
32
Views
4K
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
572

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top