N

NG1965

Hello, new to this posting malarky. I've been asked to look at an installation that was never signed off by the council, I spoke to the building inspector and we agreed a course of action, however I have an issue that I can't find an answer for in the books (not to say that I haven't missed the answer)

Customer has an oil tank 20m from house which has it's own earth rod and connection which is sound? I spoke with a tanker company who said that this was for the tanker to 'ground' on delivery. My question is I presume I will still have to bond from the CU? Supply is TT.

Thanks, Neil
 
apparently the NICEIC think it only needs bonding if it's connected to a boiler! my view is that you have to determine if the metal pipework is an extraneous conductive part. do an IR test from the main earth terminal to the metal pipe inside the house. if the reading is >22kohm, it's not extraneous and doesn't require bonding.
 
Hello, new to this posting malarky. I've been asked to look at an installation that was never signed off by the council, I spoke to the building inspector and we agreed a course of action, however I have an issue that I can't find an answer for in the books (not to say that I haven't missed the answer)

Customer has an oil tank 20m from house which has it's own earth rod and connection which is sound? I spoke with a tanker company who said that this was for the tanker to 'ground' on delivery. My question is I presume I will still have to bond from the CU? Supply is TT.

Thanks, Neil


As this bulk fuel oil storage tank is already grounded via it's ground rod, it's pipework entering the building, will almost certainly be ''extraneous'' in that it will be under 22 Kohm. So yes, any metallic pipework entering the building should be bonded in the usual manner!!
 

Reply to Oil pipe bonding in the Talk Electrician area at ElectriciansForums.net

Similar Threads

L
  • Article
Underground oil tank feed problem This unit is located in France where they use diesel not kerosene. The feed from the underground tank is not...
Replies
0
Views
156
LostinFrance
L
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
516
loz2754
L
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
537
Not really its clear in black and white. Not knowing the regs isnt the regs books fault.
Replies
10
Views
758
K
  • Article
Seeping pipe connection to Loft Cold water Had a problem with hammering noise coming from pipes (triggered by hot water, though it could be eased...
Replies
0
Views
128
KennyA
K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks