This from a PIR, Test Ref, B05, Oil Tank No Main Equipotential Bonding at Oil Reg 413-02-02
Test Ref B04, Propane No Main Equipotential Bonding at Propane Reg 413-02-02,
Provide EB,
Where would one attach bonding to these, apart from the Cylinders and fuel filter/shut off every thing is plastic Fuel oil pipes are plastic, right up to the boiler,
Gas pipes are that orange rubber stuff, So it's Metal regulator to rubber/ rubber to mainfold then copper into the building all they way to the range, So where can it be bonded that will bring it to zero potential,
Pict
Test Ref B04, Propane No Main Equipotential Bonding at Propane Reg 413-02-02,
Provide EB,
Where would one attach bonding to these, apart from the Cylinders and fuel filter/shut off every thing is plastic Fuel oil pipes are plastic, right up to the boiler,
Gas pipes are that orange rubber stuff, So it's Metal regulator to rubber/ rubber to mainfold then copper into the building all they way to the range, So where can it be bonded that will bring it to zero potential,