Jimmyb

Does a oil tank copper pipe supply need bonding if it has been put though a plastic tubing when it buried ?

Many Thanks
 
Test it, you'll soon find out if it's an extraneous earth or not!!

In practice this doesnt always work....if it's connected to a boiler or AGA chances are it'll be earthed anyway by being physically connected to a conductive part. In order for such a test to be effective you'd have to isolate it from any connected electrical earthing and bonding system from which it may get a parallel path.
 
Does a oil tank copper pipe supply need bonding if it has been put though a plastic tubing when it buried ?

Many Thanks

Is that an actual flexible conduit, or just the plastic sheath on the pipe itself?
As already stated, most oil pipes will have a continuity to earth via touching the boiler casing or simply through the water pipework. If you are getting any continuity below the magic 23k ohms then bond it.
 

Reply to Oil Supply Pipe in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

L
  • Article
Underground oil tank feed problem This unit is located in France where they use diesel not kerosene. The feed from the underground tank is not...
Replies
0
Views
156
LostinFrance
L
M
  • Article
Atkinson tank top oil feed As title anyone using one, good? bad? ugly? has to feed through a de-aireator to the boiler, but should not be a...
Replies
0
Views
94
MikeJhn
M
P
  • Article
Heating oil tank (plastic) has rusty coloured layer on bottom... Hi The tank is around 7 years old. Any ideas what causes it and/or whether it is...
Replies
0
Views
134
Plumb Line
P
A
  • Article
F&e tank vent pipe pouring hot water Hi all I have an oil fired heating system open vent with an f&e tank we had some problems with air...
Replies
0
Views
85
Andymav
A
G
  • Article
Scotland, plastic pipe? Scotland i have been told that plastic pipe is not permitted for runs through ceiling, with drops to radiators? does it...
Replies
0
Views
80
Gasinspect
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks