I currently have a 10mm T&E SWA cable (which passes through my garage) serving a small CU in my workshop at the bottom of my garden (200ft). The garage is currently connected to a FCU on the downstairs ring, but I would like to T off the SWA and add another consumer unit in the garage.

First and foremost I would like to confirm this is an acceptable thing to do in principle.

No doubt some of you will be interested in additional parameters, so to flesh things out a bit:
The SWA is connected to a 40A MCB and 30 mA RCD in a small CU that has been fitted in the meter box (independent of the main house CU). (I appreciate I will need to consider the overall load/diversity for the property.)
The workshop has a 6A lighting circuit and a 20A Radial. I am proposing to fit the same in the garage.
Oh I should mention that when the CU was fitted in the workshop an Earth Rod was added outside.

Any guidance/thoughts appreciated as long as someone answers the primary question first.
 
In principle there is nothing wrong with a submain which feeds two points.
Your post isn’t too clear as to whether it is SWA or T&E as you mention both?
 
I currently have a 10mm T&E SWA cable (which passes through my garage) serving a small CU in my workshop at the bottom of my garden (200ft). The garage is currently connected to a FCU on the downstairs ring, but I would like to T off the SWA and add another consumer unit in the garage.

First and foremost I would like to confirm this is an acceptable thing to do in principle.

No doubt some of you will be interested in additional parameters, so to flesh things out a bit:
The SWA is connected to a 40A MCB and 30 mA RCD in a small CU that has been fitted in the meter box (independent of the main house CU). (I appreciate I will need to consider the overall load/diversity for the property.)
The workshop has a 6A lighting circuit and a 20A Radial. I am proposing to fit the same in the garage.
Oh I should mention that when the CU was fitted in the workshop an Earth Rod was added outside.

Any guidance/thoughts appreciated as long as someone answers the primary question first.
I take it that you understand from the description of the intallation, that consumption of Electricity is restricted to 13 Amps, as you have taken the feed to the Shed from a fused spur from the downstairs RFC.
 
I take it that you understand from the description of the intallation, that consumption of Electricity is restricted to 13 Amps, as you have taken the feed to the Shed from a fused spur from the downstairs RFC.
I think the existing garage feed is off the FCU, the existing garden shed feed that is to be intercepted is three core SWA on a 40A MCB with a 30mA RCD.
 
I think the existing garage feed is off the FCU, the existing garden shed feed that is to be intercepted is three core SWA on a 40A MCB with a 30mA RCD.
Ah yes Rich you are right I missed that, sorry OP, message Pete999 read the bluudy post properly.
 

Reply to OK to T consumer unit for garage off existing SWA to workshop? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sounds more positive.
Replies
8
Views
629
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
534

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top