Old cu with 6mm earth - TNC-S | on ElectriciansForums

Discuss Old cu with 6mm earth - TNC-S in the Australia area at ElectriciansForums.net

T

timo

Quoting for a job. Need to install a 1 way cu to feed shower as the exising is full and old none rcd unit etc.
noticed that the C.U is 16mm tails with only 6mm main earth. Do i need to alter this or just make sure my new 1 way is 16 with 25mm tails from splitter block.
 
Size your own tails and earth according to the load on your 1 way CU,you will struggle to get 25/16 in a 1 way CU and are allowed to down rate in these circumstances...433.3.1.........434.3.
I would upgrade the existing main earth anyway,not exactly going to add much cost....and you will have to assess whether the existing 16mm supply tails to the henly will take the additional load of the shower....Dont forget the main bonding is unlikely to be adequate given the age of the install so you will need to allow for that as well.
 
true, i could use 10/16 mm tails instead. The main earth to the exising CU is quite hard to replace as it ex council and they ran them in the cavity 2 foot then into the meter box. House just been all nicely decorated and new kitechen. water and gas in 6mm too. Customer not happy about taking brand new kitchen apart to run new 10mm earth to stop tap :( hmmmm
 
I do simpathise with you and your client, but perhaps a bit of forthought may have been favourite.
Was the new kitchen decorated with additional sockets/lighting.
Hope it works out well for you and your client.
 
New kitchen looks well yes but no new sockets or light points/fittings added. Wish they had been then somone might have sorted the earth and c.u lol :)

No other way of getting a 10mm in without going through the kitchen, plus all upstairs is new laminate flooring carpets :( :(

Starting to think about losing the quote in the mail. Dont wanna but.........grrrrr JOBS!
 

Reply to Old cu with 6mm earth - TNC-S in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
349
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
896
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top