Guest569

Doing an CR on a very old period property with some very expensive original features. It has been rewired around 10 years ago but they have reused the old original switches, some of which I believe to me 70-80 years old!

A few of the switches are clearly arcing when moved so C1 noted.

What about the others that are (or appear to be) functioning ok?

These switches are pretty special but Im not prepared to put them as acceptable. A basic toggle switch won't cut it in terms of replacing them so bespoke switches likely to cost a few bob.

Replacing them is going to be a real mess/expense.

Thoughts?

Im inclined to have them down as C2.
 
He's asking about the ones that aren't arcing though. I still reckon the contact resistance is going to be high. Daz
 
Remember code 1 means danger to life or property if they are arching bad and showing signs of burning within the switch then i would say you are right with the code 1 but as for the others if they are working fine and all your testing checks out then I can't see a reason to code the others maybe put a note on the report though
 
I did not do the test , however my guy has stated when operating the switches they are crackling. Id say thats pretty dangerous...

Anyway, its the ones that appear ok Im concerned with...Should I really be saying an 70-100 year old switch is safe ?

Would appreciate if we could stay on topic with this post for a change ?
 
ok then , do the job properly and remove each switch and inspect them closely , followed by an insulation resistance test between the live parts and the casing.
at least you can then make an informed assessment on their condition before waving C1's around.
 
I did not do the test , however my guy has stated when operating the switches they are crackling. Id say thats pretty dangerous...

Anyway, its the ones that appear ok Im concerned with...Should I really be saying an 70-100 year old switch is safe ?

Would appreciate if we could stay on topic with this post for a change ?

Of course you can say a light switch is still in condition. Just because its old doesn't mean its defective. What was the resistance of the contacts of the switch in the closed position?
 
ok then , do the job properly and remove each switch and inspect them closely , followed by an insulation resistance test between the live parts and the casing.
at least you can then make an informed assessment on their condition before waving C1's around.

Please read the post again, The switches that are crackling ARE C1. The ones that I'm not sure about would be a C3 at worst, so Im not "waving C1s around"

Please read thoroughly....

Seems folk are more interested in slating my posts than trying to help!
 
Of course you can say a light switch is still in condition. Just because its old doesn't mean its defective. What was the resistance of the contacts of the switch in the closed position?

Yes, it could be fine at the time of testing but due to its age its far more likely to fail in the near future Id say. Would you reuse these switches in a rewire and issue an installation certificate based on good resistance readings at the 100 year old switches?

Lets say something goes on fire and you were the last guy to pass these 100 year old switches as "safe"? Id rather cover my --- and issue a C3.
 

Reply to Old original period light switches , condition report. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
889
Switch by the door, pendant holder and a 100W bulb, some will remember, others weren't born yet when it went out of fashion, but this was the...
    • Like
Replies
0
Views
256

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top