Something that I've never come across. RCD connected to the MET bar with a cream wire.

Can someone explain the theory for this? Earthing arrangements for combined protective and functional purpose. I can't seem to get my head round how this would work. Only thing I've come up with is that that rcd is connected to line and earth only and monitors discrepancy to earth and not N.
 
This is an electronic RCD which requires an earth reference for the phase detectors in the electronic circuit to detect the out of balance condition, similar to most RCBOs, unlike the more common toroidal current transformer type RCD. The usual reason for using electronics is to reduce the physical size of the RCD package or to speed up the operation of the device.
 
[ElectriciansForums.net] Old RCD reg?

It is a MEM but has the following numbers on it BS 4293 BS 5419 BSEN 61008 BSEN 60947-3 !!!

It is a normal size RCD got it mixed up with another one starting with a Y funny french thing!!!
 
Last edited:
Thanks MarkieSparkie and Tony, never came across one before and now I know. Cheers lads I'll research this next week when I have more time.

Ps tony is that a past paper or a testing explanation sheet in the top right hand corner? Thanks for taking the time out of your revisions. Good luck.
 

Reply to Old RCD reg? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yet another update: I believe what EDF have done is moved me from an Economy 9 to an Economy 7. I've just emailed them to ask if they can switch...
Replies
2
Views
267

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top