Hi guys,
A customer wants an old re-wireable consumer unit upgraded.
Wiring is extremely old probably 1940's. Of the two power circuits, one is the old rubber cable and one is the old red and black stranded cable.
IR tests show ok L-N L-E N-E.
Problem is the cables have no cpc on the consumer unit side. I'm getting good zs on the sockets which are twin and earth radials on the socket end (so cables must switch via a jb or something under floorboards maybe).
But I have no idea where they are picking up an earth and there is no metal conduit either.
Should I go ahead and change the unit and sign it off even though I cant put the r1+r2 readings in because there is no cpc in the consumer unit?