Hi guys,

A customer wants an old re-wireable consumer unit upgraded.

Wiring is extremely old probably 1940's. Of the two power circuits, one is the old rubber cable and one is the old red and black stranded cable.

IR tests show ok L-N L-E N-E.

Problem is the cables have no cpc on the consumer unit side. I'm getting good zs on the sockets which are twin and earth radials on the socket end (so cables must switch via a jb or something under floorboards maybe).

But I have no idea where they are picking up an earth and there is no metal conduit either.

Should I go ahead and change the unit and sign it off even though I cant put the r1+r2 readings in because there is no cpc in the consumer unit?
 
It was put on ECR report done from another electrician. He has put r1+r2 readings but i cant see how that is possible with no cpc on the other end.

He told her it needs re-wiring as have I, but she says its too much money.

She wants to get it satisfactory to rent or sell, but I am worried to put my name to it if I do the consumer unit.
 
I wouldn't do anything I couldn't be comfortable with taking responsibility for, not just electrical but any sort of work. There'll always be someone with no conscience that will do it. Alternatively see if you can pick up the t+e to bring it back to the board
 
Those rubber cables could be in any condition in the building fabric. They may be ok where they are not disturbed.
They could also be bare where they have been.
I would not be changing the board until I was satisfied wit the installation.
 
It was put on ECR report done from another electrician. He has put r1+r2 readings but i cant see how that is possible with no cpc on the other end.

He told her it needs re-wiring as have I, but she says its too much money.

She wants to get it satisfactory to rent or sell, but I am worried to put my name to it if I do the consumer unit.


What readings do you get?
 
It was put on ECR report done from another electrician. He has put r1+r2 readings but i cant see how that is possible with no cpc on the other end.

He told her it needs re-wiring as have I, but she says its too much money.

She wants to get it satisfactory to rent or sell, but I am worried to put my name to it if I do the consumer unit.

It's never going to be satisfactory with rubber cables still in service. It sounds beyond 'updating', rewire or stay clear.
 
It was put on ECR report done from another electrician. He has put r1+r2 readings but i cant see how that is possible with no cpc on the other end.

He told her it needs re-wiring as have I, but she says its too much money.

She wants to get it satisfactory to rent or sell, but I am worried to put my name to it if I do the consumer unit.

If she wants to make money she'll have to spend. Complete rewire for me. If you change the CU you'll have no idea what problems may lie ahead.
 
Hi guys,

A customer wants an old re-wireable consumer unit upgraded.

Wiring is extremely old probably 1940's. Of the two power circuits, one is the old rubber cable and one is the old red and black stranded cable.

IR tests show ok L-N L-E N-E.

Problem is the cables have no cpc on the consumer unit side. I'm getting good zs on the sockets which are twin and earth radials on the socket end (so cables must switch via a jb or something under floorboards maybe).

But I have no idea where they are picking up an earth and there is no metal conduit either.

Should I go ahead and change the unit and sign it off even though I cant put the r1+r2 readings in because there is no cpc in the consumer unit?

How do you test for IR, L-E and N-E with no earth?
 

Reply to Old rubber and stranded cables in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
772
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top