Hi guys,

A customer wants an old re-wireable consumer unit upgraded.

Wiring is extremely old probably 1940's. Of the two power circuits, one is the old rubber cable and one is the old red and black stranded cable.

IR tests show ok L-N L-E N-E.

Problem is the cables have no cpc on the consumer unit side. I'm getting good zs on the sockets which are twin and earth radials on the socket end (so cables must switch via a jb or something under floorboards maybe).

But I have no idea where they are picking up an earth and there is no metal conduit either.

Should I go ahead and change the unit and sign it off even though I cant put the r1+r2 readings in because there is no cpc in the consumer unit?
 
In a lot of older installations ,the CPC was run directly from the main earth Isco , possibly in an unsheathed cable and possibly served a few circuits , just teeing of where ever necessary


Good call,seen plenty like this,where above,maybe a modern looking semi-rewire...and below,t&e cpc arrive at a JB,and leave via an ancient un-sheathed copper conductor.

Spiders' web under floor,joined together,wrapped round a nail/screw on a joist...

Some have given better than expected readings,when tested...although, a decent fault of fair duration,would anneal it some :ihih:
 
In a lot of older installations ,the CPC was run directly from the main earth Isco , possibly in an unsheathed cable and possibly served a few circuits , just teeing of where ever necessary

I think some people referred to it as a clothesline (although having looked I have been unable to find a reference for this term).
 

Reply to Old rubber and stranded cables in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
772
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top