I have read Lennys sticky on old cables, but did red and black ever have the CPC less than 1.5 on 2.5 T&E,

Pict
 
Yes,, they used to be 1mm.. and with BS3036 fuses protecting such cable there can be issues due to the current carrying capacity under fault conditions... (gets ready to defend my new post)
 
Last edited by a moderator:
Taken from appendix c of Approved Document P.


2.5 mm2 twin-and-earth cables

incorporating circuit protective
conductor of only 1.0 mm2

For some years, 2.5 mm2 twin & earth pvc/pvc
cables to BS 6004 were manufactured with a
circuit protective conductor (cpc) of only 1 mm2,
rather than 1.5 mm2 as is incorporated today.
The size of the cpc was increased to 1.5 mm2
in BS 6004 because in certain circumstances
the 1 mm2 cpc may not always be properly
protected against thermal effects in the event
of an earth fault. This is where the cable is
used in a ring final circuit protected by a 30 A
semi-enclosed (rewirable) fuse. If this is the
case, a competent electrician should be
consulted about upgrading the cables and/or
the consumer unit.
 
Given the nominal current carrying capacity of a 1.0mm cable at 10 amps and a fusing factor of x1.5 on a rewirable fuse , ring final sub circuit = 2x1.0mm =20 amps approx, whereas the 30 am fuse actually blows at 30x1.5=45 amps, this makes a lot of sense. Thanks Lenny
 
Just thought you lot might like to know how we get from a fusing factor of approximately 2 to a correction factor for Cc of 0.725

If ff = I2/In and I2 = 1.45 Iz
Then
I2 = In * ff
so In * ff = I2 = 1.45 Iz
Therefore
In * ff = 1.45 Iz
and
In = 1.45 Iz / ff

substitute 2 for ff
and we have
In = 1.45/2 Iz
In = 0.725 Iz

So as long as the fuse rating is approximately 3/4 of the maximum current carrying capacity of the conductors the BS3036 fuse will provide overload protection

As far as earth fault protection is concerned

application of the adiabatic equation for a 30A protective device gives (√210² × 0.4) / 115 = 1.15mm²
Which means a 1.0mm2 cpc is insufficient to stop damage to the insulation of the circuit conductors

Now if a 20A (Yellow) fuse was substituted then (√130² × 0.4) / 115 = 0.72mm²

and the circuit would now comply!
 
very informative, ackbar. problem is in obtaining 20A fusewire. and before anyone else suggests it, a 15A and a 5A in parallel just ain't worth thinking about.LOL.
 
... ring final sub circuit = 2x1.0mm =20 amps approx, whereas the 30 am fuse actually blows at 30x1.5=45 amps, this makes a lot of sense. Thanks Lenny

Not forgetting that rings are rarely completely balanced in practice - most likely one leg of the 1mm would carry more than an exact 50% of a fault current, especially in a badly-designed installation with, for example, a kitchen, or a heavy fixed load at one end of the ring.

BTW, for £5 here's enough 20A fuse wire for a lifetime :)

TLC-direct .co .uk / products / TLFW20.html
 
Last edited:

Reply to old T&E in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Does it really actually need earth sleeving inside the tube? I know it feels a bit bodgy but what's going to happen and isn't an unbroken...
Replies
9
Views
559

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top