It was a long time before i came into the industry that water and gas services were allowed to be your sole means of earthing to a property. What you may be finding, is examples of those bygone years. Far more likely your seeing unauthorised connections to service pipework!! ...lol!! It's still allowed on privately derived water systems, if they meet the criteria....
Supplementary bonding has never been a problem to incorporate but again, not as your sole means of earthing. Structural steelwork also can't be your CPC, it can however be your bonding conductor connection to equipment etc. All normal circuits need to incorporate a CPC from the installations MET/MET be it a TT, TN-S, TNC-S earthing system. That has been the rule from early 13th edition Reg's, where a CPC has been required. (not required on lighting circuits till late 13th early 14th ed Regs, late 50's ish lol!!)