Can anybody help, I am looking to rewiring an old three storey house for a friend. I've not been in the trade very long. I am looking at an old fuse box with a cut out with a YEB sticker over, which gives you an idea how old the cut out is. There are two cables entering the cut out and two exiting it, to the meter. There is no sign of an MET or indications of a TT. I have not removed the cover yet. Can anybody suggest what type of system I have here. The only sign of an earth is a 2.5mm wire from a water pipe going into the back of the old fuse box. Would I need to contact the DNO to have this altered.
:hammer:
 
No main earth.

Typical of the Harehills and Roundhay Park area of Leeds, ask anyone that has worked these areas. 9 times out of 10 you can get a great Ze with a 3ft rod. 2 months ago I got 0.27 due to the moist earth under the cellar floor.

Sounds like the OP just needs a TT setting up. Send me a PM and I'll pop around on the way home from work and have a look at it for you free of charge.
 
That bare wire will almost certainly be the original 3/029 or 7/029 earthing conductor connecting the installation to the means of earthing (the towns metal water main)
In modern parlance it would be called a TT system, but in hose days I don't think they had such acronyms.
 
If the service head is cast iron and has rewireable fuses for both line and neutral get the DNO in to change the service head out (free of charge). At the same time you can enquire if the supply network to this house has a PME/TNC-S connection available....
 
I'm with eng 54, phone the DNO up and they will probably come and change the cutout free of charge and at the same time give you TNC-S/PME if available. I've seen many of this style with no bushes or grommets where the tails pass in and out of the metal enclosure, VIR tails from the cutout to the meter,etc and are normally in such a poor state that you wouldn't want to leave it in place.
 

Reply to Old YEB fuse box in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
413
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
The last couple of de-loops that I have been involved with had the single phase supply replaced with a three phase cutout (as I believe the DNOs...
Replies
5
Views
1K
yeah so it looks like an old off peak heating circuit to what would have been storage heaters my preference is to remove them completely from the...
Replies
2
Views
291

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top