Hi all,
My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an installation. Am I right in saying that DNOs allow this for meter tails, due to the maximum length of 2 or 3m, insulated and sheathed nature of the tails and the relatively low chance of a fault occurring?
For a domestic installation, the norm is to install 25mm live conductors and 16mm earthing conductor from the meter to the consumer unit, in case a 100 amp HRC fuse is installed by the DNO, and to future proof the install for future loads etc.
That's all and well, but what is the correct selection of tail CSA for extra consumer units. Maybe an extremely low load off peak contactor control DB, or a new electric shower board? In these cases, we know that overloads are impossible due to the nature of the loads; therefore we can workout the design current and choose a size of tails to use, assuming a 1 way CU is used (no spare ways).
A load of 8.5kW @ 230v = 37A, therefore we can use an mcb of 40A. 10mm^2 tails would be adequate to carry the load. However, if we split the meter tails into a henley block, those 10mm tails may now be "protected" by a 100a DNO fuse. Is this acceptable? I personally don't like the thought of this, but on the other hand I can see how stupid it would be to install 25mm tails for a 1 way 40A CU. THEORETICALLY, if the design current was 6 amps for instance, could 1.5mm^2 tails be used to supply a 1 way CU with a 10A mcb?
I understand that adiabatics may be used to see if the live tails and protective conductor could withstand the potential fault current until the DNO fuse blew etc, but is this fault protection by the DNOs fuse allowed to be omitted anyway?
With regards to consumer units where overloads are possible (socket circuits maybe), surely you could apply diversity, calculate a maximum demand, then size the tails to the expected demand of the new CU? If these live tails are again, less than 25mm^2 on a 100a DNO fuse, do we have the same problem? Obviously overload protection would have to be provided for the final circuits with the potential for overload, in the CU.
I am sorry about the length of my post. Hopefully this makes sense to people too, haha. This is my first post so thank you for having me.
Thank you.
My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an installation. Am I right in saying that DNOs allow this for meter tails, due to the maximum length of 2 or 3m, insulated and sheathed nature of the tails and the relatively low chance of a fault occurring?
For a domestic installation, the norm is to install 25mm live conductors and 16mm earthing conductor from the meter to the consumer unit, in case a 100 amp HRC fuse is installed by the DNO, and to future proof the install for future loads etc.
That's all and well, but what is the correct selection of tail CSA for extra consumer units. Maybe an extremely low load off peak contactor control DB, or a new electric shower board? In these cases, we know that overloads are impossible due to the nature of the loads; therefore we can workout the design current and choose a size of tails to use, assuming a 1 way CU is used (no spare ways).
A load of 8.5kW @ 230v = 37A, therefore we can use an mcb of 40A. 10mm^2 tails would be adequate to carry the load. However, if we split the meter tails into a henley block, those 10mm tails may now be "protected" by a 100a DNO fuse. Is this acceptable? I personally don't like the thought of this, but on the other hand I can see how stupid it would be to install 25mm tails for a 1 way 40A CU. THEORETICALLY, if the design current was 6 amps for instance, could 1.5mm^2 tails be used to supply a 1 way CU with a 10A mcb?
I understand that adiabatics may be used to see if the live tails and protective conductor could withstand the potential fault current until the DNO fuse blew etc, but is this fault protection by the DNOs fuse allowed to be omitted anyway?
With regards to consumer units where overloads are possible (socket circuits maybe), surely you could apply diversity, calculate a maximum demand, then size the tails to the expected demand of the new CU? If these live tails are again, less than 25mm^2 on a 100a DNO fuse, do we have the same problem? Obviously overload protection would have to be provided for the final circuits with the potential for overload, in the CU.
I am sorry about the length of my post. Hopefully this makes sense to people too, haha. This is my first post so thank you for having me.
Thank you.