Am i right in saying that off load switches break the neutral and line feed, and on load switches just break the line?

doing my 2330 303 exam on tuesday!!
 
and also why do the continuity tests have to be done first - is it because it is the most common to have a fault there? so process of elimination or is there a scientific reason?
Thanks in advance :)
 
An on-load switch can be switched while there is a load present for example a light switch, an off-load switch should only be switched when there is no load, for example a 3phase isolator on a motor circuit.
continuity of cpcs is done 1st to check just that, if there was a break in the cpc and you powered up straight away there is a potential danger, the cpc is the protection of the circuit, so if its not there, you may be putting your or someone else's life in danger.

Danny
 
Last edited by a moderator:
An on-load switch can be switched while there is a load present for example a light switch, an off-load switch should only be switched when there is no load, for example a 3phase isolator on a motor circuit.
continuity of cpcs is done 1st to check just that, if there was a break in the cpc and you powered up straight away there is a potential danger, the cpc is the protection of the circuit, so if its not there, you may be putting your or someone else's life in danger.

Danny

thanks for replying - just one thing though - Why is it before say the ~IR tests though?
 

Reply to On Load v Off Load in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It does seem to me that there's a capacitively coupled voltage to each set of downlights (on the light side of the switch), and when you put the...
Replies
6
Views
286
Also posted in DIY. strange one in my kitchen. 3 sets of 2-way switched mains GU10 Philips down lighters. ( no dimmers) Have been fine for...
Replies
0
Views
156

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top