lofty84

A circuit is protected by a 32A type B breaker. if the value of Ze is 0.8 ohms what will be the maximum allowable value for (R1+R2)


how do I go about finding this in the IEE regs (red one) please ......
 
your max. value for Zs is 1.44ohms ( table 41.3. 32A type MCB). therefore use Zs=Ze+(R1+R2)
 
Last edited:
Its in the regs table 41.3 pg. 56. These values are given at fault conductor operating temp. Where as the ones in OSG are at 80% compared to the regs which are given at normal operating temp.

Sent from my GT-I9100 using Tapatalk
 
cheers telectrix and Si jacc ;-).

So with those details the maximum allowable R1+R2 value is going to be 0.64 ohms

1.44 - 0.8 = 0.64 ohms



well that was nice and easy
 
Last edited by a moderator:
32A x 5 = 160 230/160=1.44 x0.8 =115 ohms is you max allowed take away 0.8 = 0.35 / by cable in table 9A osg will = your length
 
why use the 0.8 value. the question asks for the max. value. the max. value for Zs is 1.44.
 
my answer sheet says the correct answer is 0.64 ohms and that worked with what telectric and SI were saying. i = P/u u have just messed that up lol, how come you are timesing the 32A breaker by 5 snd doing all the other maths.......
 
my answer sheet says the correct answer is 0.64 ohms and that worked with what telectric and SI were saying. i = P/u u have just messed that up lol, how come you are timesing the 32A breaker by 5 snd doing all the other maths.......

.64 ohms if the ze measured is .8 , max r1+r2 depends on what the measured ze is??
 
.64 ohms if the ze measured is .8 , max r1+r2 depends on what the measured ze is??

if you don't have the brb to hand, you can calc. the max. ZS for any MCB . it's 230/( 5 x In ) for a B type, for c and d types the factor 5 becomes 10 and 20 respectively.
 
I see so if I had a 40 A type d breaker and I wanted to know the max zs I can go

230/40X20 = 0.2875

doesnt sound right to me ...
 
Last edited by a moderator:

Reply to the thread, titled "one of many to follow Im sure but ......" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top