Darkwood
Got a new customer and in short I wired up an old lathe to its new position, on commisioning I noted that th old electrics were dated and had illegal additions...
The motor run was a physical switch that just energised the coil of the contactor direct.
The E-stop just interupted the switch
So a power failure and power return would start the lathe without warning and also closing the E-stop would also start the lathe back up ... that aside when testing the Estop it was reset and because the lathe wasn't in Neutral for starting it took out the mcb because it was DOL on load.....thats the background and my field so easy fix for me, the strange thing is when the TP Merlin mcb tripped it also tripped the adjacent DP rcd unit .....
Discuss why! (ps the rcd fed sockets and no earth leakage was the cause of its trip)
PS I know the reason but wondered if anybody can come up with the theory of why a mcb tripping for known reasons tripped an adjacent rcd unit.
The motor run was a physical switch that just energised the coil of the contactor direct.
The E-stop just interupted the switch
So a power failure and power return would start the lathe without warning and also closing the E-stop would also start the lathe back up ... that aside when testing the Estop it was reset and because the lathe wasn't in Neutral for starting it took out the mcb because it was DOL on load.....thats the background and my field so easy fix for me, the strange thing is when the TP Merlin mcb tripped it also tripped the adjacent DP rcd unit .....
Discuss why! (ps the rcd fed sockets and no earth leakage was the cause of its trip)
PS I know the reason but wondered if anybody can come up with the theory of why a mcb tripping for known reasons tripped an adjacent rcd unit.