Ok, need to bounce ideas about if poss....

Existing building with 3ph TT supply (100mA RCD, non -S type), feeds another building 300m away with a 3ph sub DB (no RCD) where my customer is looking to fit a 50kWp PV feed to.

We're waiting on Ze values on the incomer. I have no other info at the moment.

Thoughts/concerns with feeding the PV into the sub DB?
 
all depends on the CSA of the cable feeding the sub db, if that's ok for a 300m run then go for it, but maybe up the RCD to 300mA if that's ok for all other reasons.
 

Reply to opinions please? in the Green Lounge (Access Only) area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top