Installation is in a large, period domestic dwelling. Property rewired 2007. The final ccts for the main house are supplied by the 16th Ed. split-load CU seen at the top of the pic, with Max demand for the main house reasonably assessed as not too far off the 100a mark.
The 3 phase supply was installed last year - it was suggested by the installer, in order to supply a dedicated sub-main to an annexed cottage. The cottage has it`s own D/B, with a 30mA RCCB incomer supplying B32`s for cooker & rfc, and B6 lighting circuits (x2). Extraneous-conductive (water service in metallic pipework) parts in evidence thru-out the cottage.
For clarity, the new dist.cct for the cottage has actually been supplied from the 30mA RCD protected side of the main board, running in 10mm T&E from a B50 to the 3 Henleys . As can be seen, its fed from there into 3 core 16mm XLPE which drops (with no further support) the 2m to the concrete floor.
It then terminates into an external 300x300x150 insulated enclosure on an external wall, and connects to an outgoing SWA (same 3c x 16mm) via Weidmuller type disconnect terminals. These DIN rail terminals are in free air within the box, held in position simply by the cores attached to them. No end plates are fitted.
Correct CW25 glands are fitted to each of the 2 SWAs at this box, but no banjo`s, and no other means to achieve continuity between the armour of each sheath. The entry hole for one has been drilled into the reinforcing ribs, so the galv backnut can`t be tightened flush.
Termination at the cottage`s CU is unclear. The supply 3c X16mm cores eventually re-appear close to the all insulated D/B, but the armour, inner & outer sheaths, are all hidden within the partition wall.
I`ll say nothing more at this stage, other than to invite your comments. At some point soon i`ll be in a better position to explain more fully.
Installation is in a large, period domestic dwelling. Property rewired 2007. The final ccts for the main house are supplied by the 16th Ed. split-load CU seen at the top of the pic, with Max demand for the main house reasonably assessed as not too far off the 100a mark.
The 3 phase supply was installed last year - it was suggested by the installer, in order to supply a dedicated sub-main to an annexed cottage. The cottage has it`s own D/B, with a 30mA RCCB incomer supplying B32`s for cooker & rfc, and B6 lighting circuits (x2). Extraneous-conductive (water service in metallic pipework) parts in evidence thru-out the cottage.
For clarity, the new dist.cct for the cottage has actually been supplied from the 30mA RCD protected side of the main board, running in 10mm T&E from a B50 to the 3 Henleys . As can be seen, its fed from there into 3 core 16mm XLPE which drops (with no further support) the 2m to the concrete floor.
It then terminates into an external 300x300x150 insulated enclosure on an external wall, and connects to an outgoing SWA (same 3c x 16mm) via Weidmuller type disconnect terminals. These DIN rail terminals are in free air within the box, held in position simply by the cores attached to them. No end plates are fitted.
Correct CW25 glands are fitted to each of the 2 SWAs at this box, but no banjo`s, and no other means to achieve continuity between the armour of each sheath. The entry hole for one has been drilled into the reinforcing ribs, so the galv backnut can`t be tightened flush.
Termination at the cottage`s CU is unclear. The supply 3c X16mm cores eventually re-appear close to the all insulated D/B, but the armour, inner & outer sheaths, are all hidden within the partition wall.
I`ll say nothing more at this stage, other than to invite your comments. At some point soon i`ll be in a better position to explain more fully.