Just been flicking through and table 7.1 to enable final circuits to be installed without calculating voltage drop has one of the criteria as
ii)The final circuit is connected to a dis board or CU at the origin of the installation
Just seeing that I understand this and the reasoning behind it correctly really. If you had the supply in to a large house with the meter and main board in the cellar, and 2 submains fed from this main board in the east and west wings of the house (think Wayne manor), this means that the table in the OSG can't be used for any final circuits from either of the submains.
Have I got this correct and is the reason that we also need to take the voltage drop of the distribution circuit into account?, so obtaining an accurate voltage drop from the origin of supply to the extremity of the final circuit we're installing?
If I am right with this, would it be acceptable to measure the voltage drop of the distribution cable as I can't see how this could be calculated without knowing an accurate length, size and condition.
Likewise in commercial installations where a final circuit can be installed to a submain that is in essence daisy chained through several other submains and control boxes (for example DB5A2), how would you go about calculating the overall voltage drop on the circuit you're installing?
Thanks
ii)The final circuit is connected to a dis board or CU at the origin of the installation
Just seeing that I understand this and the reasoning behind it correctly really. If you had the supply in to a large house with the meter and main board in the cellar, and 2 submains fed from this main board in the east and west wings of the house (think Wayne manor), this means that the table in the OSG can't be used for any final circuits from either of the submains.
Have I got this correct and is the reason that we also need to take the voltage drop of the distribution circuit into account?, so obtaining an accurate voltage drop from the origin of supply to the extremity of the final circuit we're installing?
If I am right with this, would it be acceptable to measure the voltage drop of the distribution cable as I can't see how this could be calculated without knowing an accurate length, size and condition.
Likewise in commercial installations where a final circuit can be installed to a submain that is in essence daisy chained through several other submains and control boxes (for example DB5A2), how would you go about calculating the overall voltage drop on the circuit you're installing?
Thanks