Table 7.1(i) lists standard circuits that can be installed without calculation. The radial circuits are all listed as having a terminal load. Can they equally be used for socket circuits? Just to settle an argument!
 
dont like table 7.1 as not all the circuits work out for volt drop even though they are stated as ok , best do it the right way imo
 
Table 7.1(i) lists standard circuits that can be installed without calculation. The radial circuits are all listed as having a terminal load. Can they equally be used for socket circuits? Just to settle an argument!

The lengths given will be worst cases. I would say that if the total load (Ib) is at the end of the radial, the circuit will be carrying full current along its entire length, which will result in a shorter circuit length to keep VD<5%. If that makes any sense!!!

But yes, they can be used for socket circuits.
 
The lengths given will be worst cases. I would say that if the total load (Ib) is at the end of the radial, the circuit will be carrying full current along its entire length, which will result in a shorter circuit length to keep VD<5%. If that makes any sense!!!

But yes, they can be used for socket circuits.

Yes, that's perfectly logical.

Morph, I have never used the table, but was having a look through the green OSG (only just 'upgraded' from red) and was wondering why they included it.......yes it makes life easier, but I would only trust my own calcs for a circuit I'm installing. It seems to be aimed at folks who don't know how to calculate voltage drop, select the correct cable etc. You say the voltage drops don't always work out....this in itself to me is a major issue with this table.
 
Yes, that's perfectly logical.

Morph, I have never used the table, but was having a look through the green OSG (only just 'upgraded' from red) and was wondering why they included it.......yes it makes life easier, but I would only trust my own calcs for a circuit I'm installing. It seems to be aimed at folks who don't know how to calculate voltage drop, select the correct cable etc. You say the voltage drops don't always work out....this in itself to me is a major issue with this table.

its just a quick reference guide, guide being the operative word... always best to calc the circuit yourself...
 

Reply to OSG Table 7.1(i) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
701
  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
108

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top