Hi folks, went to see a board change today at the moment it's bs3036 fuses. only major problem that came up was new bathroom circuits(shower/light) had been installed via a 2way type b rcd unit.......

But the cables are about a foot short from current db position. I'm planning in installing a 11way Wylex rcbo board, so I don't fancy having two rcbo/rcds in line. Was thinking about supplying the shower unit with a 45/50 amp mcb. Supply circuit will run surface (all 1foot of it) and not supply sockets so I'm saying doesn't need rcd protection?
Other way is a junction box, but tbh I don't fancy that.
Last option I had thought of was to make the supply to the rcd unit a 40amp rcbo type c/d zs permitting?

anything obvious I'm missing?

thanks
 
Your right in saying the surface supply to the shower board does not require RCD protection provided the info given is correct. Are you installing a duel RCD unit? If not just feed from non RCD side. Otherwise as you said join/extend the shower cable. Wago din rail enclosure.
 
For the sake of one 60A junction box and a little one for the lighting, I'd just tidy it up into the one new CU.

Sometimes there's a good reason to have multiple boards, but one new board with some spare ways is how I'd do it.

Not in a standard sized house there isn't!! lol!!

As for the OP, ....extend the two existing cables using a suitable enclosure and connection methods into the new CU, ....Job done!!
 

Reply to Other Options in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
940
  • Question
What I find a little bit interesting is that there was an era of MFT's e.g. Robin, early Kewtech that tried to do non-trip loop tests using D-Lok...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top