paul_h
Hi folks, went to see a board change today at the moment it's bs3036 fuses. only major problem that came up was new bathroom circuits(shower/light) had been installed via a 2way type b rcd unit.......
But the cables are about a foot short from current db position. I'm planning in installing a 11way Wylex rcbo board, so I don't fancy having two rcbo/rcds in line. Was thinking about supplying the shower unit with a 45/50 amp mcb. Supply circuit will run surface (all 1foot of it) and not supply sockets so I'm saying doesn't need rcd protection?
Other way is a junction box, but tbh I don't fancy that.
Last option I had thought of was to make the supply to the rcd unit a 40amp rcbo type c/d zs permitting?
anything obvious I'm missing?
thanks
But the cables are about a foot short from current db position. I'm planning in installing a 11way Wylex rcbo board, so I don't fancy having two rcbo/rcds in line. Was thinking about supplying the shower unit with a 45/50 amp mcb. Supply circuit will run surface (all 1foot of it) and not supply sockets so I'm saying doesn't need rcd protection?
Other way is a junction box, but tbh I don't fancy that.
Last option I had thought of was to make the supply to the rcd unit a 40amp rcbo type c/d zs permitting?
anything obvious I'm missing?
thanks