Outbuidings Lighting

T

TimmyB

Doing work in outbuildings (No Gas or Water supplies) sockets on RCBOs but thinking lighting can be MCBs
anybody agree with that
 
Yes, no need for RCD protection of lighting circuits if run on the surface. No particular requirement for mechanical protection unless the location demands it.
 
Doing work in outbuildings (No Gas or Water supplies) sockets on RCBOs but thinking lighting can be MCBs
anybody agree with that

If mechanically protected yes.

Yes, no need for RCD protection of lighting circuits if run on the surface. No particular requirement for mechanical protection unless the location demands it.

nobody seems to be asking what the earthing system is here?
 