Doing work in outbuildings (No Gas or Water supplies) sockets on RCBOs but thinking lighting can be MCBs
anybody agree with that
anybody agree with that
Doing work in outbuildings (No Gas or Water supplies) sockets on RCBOs but thinking lighting can be MCBs
anybody agree with that
If mechanically protected yes.
Yes, no need for RCD protection of lighting circuits if run on the surface. No particular requirement for mechanical protection unless the location demands it.
nobody seems to be asking what the earthing system is here?