Did you have a test result for the suspected extraneous metal work? You'll have to decided whether to export your TNC-S supply or not to your shed. Any extraneous metal work may have an impact on your decision.

You're not exporting anything, just extending the equipotential zone.
 
Extraneous.

So, SWA from MCB, with NO connection to MET at CU, then RCD garage board with rod at shed???

Will that provide the RCD required for regs between CU and shed, or would that only RCD the shed itself?

No, to create a Seperate TT earth the armour must be connected to the earthing system of the installation it is fed from and must meet the requirements of a cpc (or have a core used as a cpc connected) this then would be isolated at the load end with a plastic gland/heat shrink etc and a separate earthing system create by use of multiple properly installed earth rods.
 
You say to-may-toes and I say to-mah-toes. Ohh, how tiresome.



You said 'exporting the TN-C-S supply'

I said 'extending the equipotential zone'

I wasn't being flippant like your reply, just simply pointing out the error.
 
Last edited:
You said 'exporting the TN-C-S supply'

I said 'extending the equipotential zone'

I wasn't being flippant like your reply, just simply pointing out the error.
Don't understand the error; I've see both phrases used for the same procedure. Could you explain the difference for me. Always willing to learn by my mistakes.
 
Don't understand the error; I've see both phrases used for the same procedure. Could you explain the difference for me. Always willing to learn by my mistakes.


You cant export the TN-C-S as this stops at the service head. It is then TN-S inside the property. So the circuit supplying the outbuilding/shed, from the consumer unit, or possibly a switch fuse, is a TN-S arrangement also.

Extending the equipotential zone is the correct terminology.
 
Last edited:
Hi

You dont export/extend an equipotential zone, you create one, and i suggest that you do indeed export the pme, reason being is that all your exposed and extraneous condutive parts are still connected to a PME service head so needs to be treated as such.

Cheers
 
it's a question of terminology. if i export something, then it goes away, nothing remaining. like if i sold something to a company in china. nothing would remain here. so i concur with extending the equipotential zone. or creating a new EZ and combining with the opriginal.
 
it's a question of terminology. if i export something, then it goes away, nothing remaining. like if i sold something to a company in china. nothing would remain here. so i concur with extending the equipotential zone. or creating a new EZ and combining with the opriginal.

Hi

No, you create an equipotetial zone, it doesnt just appear. Export means to transfer, and in this context it is the earthing system and the neutral potential which is being exported.

Cheers
 
just what i mean. the pme is not transferred, as it remains where it is. it's just extended/expanded.
 
Just to add my two penneth, seeing's though I started the discussion on exporting/extending.
IMO the supply, any supply stays in it's form, wherever it is in the installation. For example, TNC-S supplies to permanent buildings on caravan sites, remains a is. The supplies to actual caravans are then converted to TT. TNC-S supplies between buildings are still TNC-S, and relevant regs apply.

As for the phrases; 'exporting TNC-S supply' & 'extending equipotential zone', I've seen both used & quoted. However, only in discussion forums etc. I can find neither of those phrases used in BS7671 (large document mind), nor guidance note 8, for example. Just reference to the correct use of earthing arrangement.

Hence in my opinion, each phrases are both right and both wrong. :)
 
Okay, so terminology aside. I've had a shifty of the cable route etc too now. So the final job is...

SWA approx 50m from house to shed.
Supply is confirmed PME.
Metal frame is extraneous

Option1
MCB (with RCD main)at CU, 10mm SWA, bond at shed

Option2
MCB (no RCD) at CU, 4mm SWA, rod at shed
 
Option 3
Install conduit from house to shed.
MCB (no RCD main)at CU, 4mm SWA, 10mm Earth, bond at shed
Then you can add extra cables (like alarm, phone, Ethernet) at a later date.
 
A) Take from MCB, then SWA down to RCD protected garage board with localised earth rod.

I would say this (but may not need localised earth rod, although you could always additionally have an earth rod), but taken from a fuse or MCCB - not an MCB. MCBs in series will not discriminate under fault conditions.
 

Reply to Outdoor Building Power in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
987
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
635
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top