Hi all

The subject says it all - there's a lot of outside exposed clipped t&e out there with all the attendant physical protection and UV issues.

Question is - should it have a fault code on a report? I guess it would be a C3 at most, but should it feature at all?

Cheers
 
If it’s a short stretch of cable from say a hole to a light then no code

if its yards of cable clipped all around the house getting baked in the sun but no visible damage then code3

if It’s visibly badly damaged And crumbly to the touch then code2
 
Depends, on a few factors...
Use your engineering judgement and be confident in your decision.
Books are good for guidance but they cant account for every situation.
You could code this C1 C2 or C3. Maybe no code.

I'd check If it's all gone brittle or not, and where it is? I'd personally code it differently depending on risk.
If it's at a school where kids might pick snd pull at it you may want to code it as a C2.
A small section going into a 500w flood light high level in someone's back garden in good condition is probably most likely ust a C3
 

Reply to Outdoor t&e - EICR fault code? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
True. Although I'd hazard a guess that things like woodworm treatment are probably chemically quite similar? Don't know.
Replies
13
Views
1K
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
303

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top