sparks1234

-
Arms
I know you will ask and for the life of me I cannot remember where it is TNCS or TNS.
But

If you were installing various submains to stables / store huts etc from a central dis board.

Its generally for lighting with a few sockets here and there.

Would you create individual TT systems?
 
Sorry, try to explain better.

Assume we have a TNS system in a building, the building has many outbuildings anywhere from 15 to 70 mtrs away.
there are to be sub-mains cables for small consumer unit to feed lights and some sockets, would you create an individual TT to each outhouse? or would you use the earth from the main dis board?

Its the PME TNC-S system you shouldn't export the earth.

So ok then if it is a PME then create a TT system to each outhouse so the original earth is not used.
 
Last edited:
Hi


TN-C-S supplies don't go well with farms, if it is TN-C-S you can supply the farm house and then supply the outbuilding and barns with local earth electrodes (TT installations). Don't interconnect the earthing systems though.


Question ....Do you guys use the TN-C-S earthing to protect the submain to the outbuildings? or do you dump the TN-C-S system and just use TT and interconnect.

Electro
 
TT all the way for me too.:)

Reason being the amount of steelwork likely to be found in an agricultural situation i.e, pens, gates, structural steel etc etc.


I think section 705 says something about not using TN-C-S in agricultural unless there is an earthed metal grid in the floor used as an extraneous conductive part.


Your situation does seem to be different, a TN-S would be fine, if not then TT.
 
Last edited by a moderator:
Hi

Question ....Do you guys use the TN-C-S earthing to protect the submain to the outbuildings? or do you dump the TN-C-S system and just use TT and interconnect.

Electro

Guys what are your views on earthing submains from TN-C-S supplies , and what are your views on TNS supplies to outbuilding not necessarily farms..


Appreciated your opinions

electro
 
Earthing the armourings of an swa for instance, with the main supply earthing system is fine, as long as they are isolated at the other end (if the job requires it).

No problem with using a TN-S system anywhere, size conductors accordingly and away to go.:)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sparks1234

Arms
-
Joined
Location
Hertford
Website
http://www.a2electrical.co.uk
Business Name
A2electrical.co.uk

Thread Information

Title
Outhouse wiring
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
sparks1234,
Last reply from
Guest123,
Replies
8
Views
4,078

Advert

TrueNAS JBOD Storage Server

Back
Top