outside boiler rcd clarification | on ElectriciansForums

Discuss outside boiler rcd clarification in the Australia area at ElectriciansForums.net

L

littleeley

if an oil boiler was in the kitchen of a house wired back in the seventies on pme earthing 6mm to bond water and oil line ect with no earth trip and the boiler was going to be replaced with an outside boiler as the boiler would have to be rcd protected is it ok to replace the fsu with a rcd protected fsu and would the earth bonding have to be up dated from 6mm to 10 mm as not sure were you draw the line with keeping it compliant when only alterations are required like adding exstra socket on ring rcd protect the ring ok do you need or should you up date the earth bonding your thoughts on this would be apreciated
 
First off does the new outside boiler need to be RCD protection.

Reg 131.8 tells us that yes for alteration or additions then the earthing and bonding arrangements shall be adequate.

Reg 544.1.1 tells us that a bonding cable must be sized in relation to the neutral of the DNO supply cable and often than not that is a 10mm.

As Tel says you can risk assess the conductor and keep that 6mm, but IMO it is best to adhere to the regs as often as not.
 

Reply to outside boiler rcd clarification in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
184
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
496
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top