H

hightower

Went to a job last week, replace an outside light with another customer bought one. Straight swap, few extra holes in the wall for new mounting, job done. Photocell model.

Left the job with a working light. Now, I fitted this in the p***ing down rain, which in itself was a tad silly of me but I wanted this job out the way. I chalked it off as something damp inside and said I'd be back round to look in a few days when it dried up - not a problem as it has a switch so can be isolated leaving the rest of the electrics on and working.

When I went back it hadn't rained since fitting, so should have been nice and dry in there by now. I checked and there was no wires trapped or anything. I'd asked if they'd tried it since and "no", so flicked it on and it works. Left the job, 10 minutes later a message to say it's tripping again.

So the symptoms are the light works fine for a little while, but then starts tripping. Once it starts tripping it continues tripping until seemingly left a while.

Probably a simple one as "dodgy fitting" but wanted to double check on here if anyone had any more thoughts? He's asked me to stick his old one back up, which I'll be doing this weekend at some point, but wanted a second opinion....
 
The light itself is unlikely to have any connection to earth in the circuitry so unless something is expanding whilst on and the circuit/lamp is then touching the body of the fitting I cannot see how the RCD would trip from the light fitting alone.
Where did those extra holes for mounting the fitting go? perhaps near the supply?

Also if the light had been changed before and there is a nice terminal block in insulation tape just inside the wall that got wet during fitting this may be a cause.
On site investigation is the only way, though it would be interesting to see if it still trips with the old light!
 
The light itself is unlikely to have any connection to earth in the circuitry so unless something is expanding whilst on and the circuit/lamp is then touching the body of the fitting I cannot see how the RCD would trip from the light fitting alone.
Where did those extra holes for mounting the fitting go? perhaps near the supply?

Also if the light had been changed before and there is a nice terminal block in insulation tape just inside the wall that got wet during fitting this may be a cause.
On site investigation is the only way, though it would be interesting to see if it still trips with the old light!
The cable is straight through so no chance of contact. Just finding it strange with it being a delayed trip rather than the second it's turned on
 

Reply to Outside light - tripping RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Sounds like it didnt live up to its IP65 rating. If under warranty get Amazon to replace it.
Replies
5
Views
521
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
350

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top