Happy Easter All

Received a call from a Plumber who has just installed a new outside boiler for a customer, he has reported getting an electric shock from the boiler case!

Had a quick look on Saturday in order to quote, found the following: -

1) Boiler outside being supplied by 3C&E flat cable dangling on the ground through the wall to CU protected by 16A MCB (No RCD protection)

2) No bonding to any boiler pipes or oil pipe, bonding to Cold Main water pipe only.

My questions are:

1) What tests should I carry out to confirm he did receive a shock?

2) What do you suggest to do regarding cable (SWA etc)

3) As the boiler is outside and the oil line does not go into the house will it require bonding?

4) What about RCD protection?

5) Would it be wise to install some kind of Isolator outside at the boiler for maintenance purposes?

Any help greatly appreciated as always.

Mark
 
As above,R1R2 test as well. The oil line will not require bonding but metallic pipes coming from the boiler into the building should be treated as incoming services and main bonded at the point of entry.
I'ts not a special location under bs 7671 just because it's outside, and if a TN system and surface wiring no rcd protection is required. I would though in this case to cover yourself, as a shock has been reported and something may be missed or not show up on tests and inpections.
Check in particular continuity to the boiler case....there may be an earth link not fitted,also possibility of a pinched wire when the case fitted.
 
Last edited by a moderator:
I would first of all check that your plumber friend has connected that 3 core up correctly as he obviously connected it to fire up his new boiler.


Are there no controls inside the house for this boiler.....stat, timeclock etc???
 

Reply to Outside Oil Boiler in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
319
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
846
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
968

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
T
  • Article
New plumbing & heating system advice Hello, I'm installing a new central heating & plumbing system and just wanted to run through my design...
Replies
0
Views
226
Tommyh311
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top