i have been asked to supply power to an outside event i have made a small board comprising of 4 double sockets and one 16 amp socket all on
16 amp rcbo,s . It will be fed from a 40 amp 60898 mcb am i correct in saying that the main switch on my board needs to be a 100mA or greater rcd
rather than a standard 60947-3

thanks
 
Hello all
i have been asked to supply power to an outside event i have made a small board comprising of 4 double sockets and one 16 amp socket all on
16 amp rcbo,s . It will be fed from a 40 amp 60898 mcb am i correct in saying that the main switch on my board needs to be a 100mA or greater rcd
rather than a standard 60947-3

thanks

I assume the 4 double sockets are the normal BS 1363 type and therefore will be used for outside equipment less than 32 amps, therefore you will need to provide them with 30mA additional protection

Not sure if your a sparks or not, but a 100amp 60947-3 will have no mA rating. If your asking if you should fit a switch larger than 100 Amps then no because you have said earlier that this board is being fed by a 40amp MCB, so you will never exceed the 100amps that a 60947-3 is rated for
 
A 60947-2 is an MCCB while the quoted 60947-3 is a normal switch.

The cable feeding your board should be protected by one of the following either a BS 60947-2 which is an adjustable MCCB, the type that have the dials on it, or an S type RCD which is the time delay type. This is order to have discrimination with your 30mA RCBO's
 

Reply to outside supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
207
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top