Morning lads.
Todays job is to go to in laws and firstly replace a cooker hood that went fzzzzz! Which is straightforward.
But I’ve also got to change the gas hob for an electric. Following an incident where gas was left on by increasingly forgetful mother in law.
There is an existing 32A protected, 6mm cable cooker supply switch that controls a double oven at the moment…. Total rated load 4.8kW
The new hob is 5 ring ceramic, rated 7350W
What’s the diversity on a 5 ring hob, and could it share the cooker supply? Even if I update the 32 to a 40. (Old mk sentry board, hoping I’ve got spare mcbs)
I’m all set to run in a new 6mm through the wall into the garage and back to the board… but wanted to save a bit of time with this being a family job.
Cooker diversity calculations were framed before the era of separate hobs and ovens, but as long as they're installed oven below hob, as they would be on a conventional slot in cooker, then I'm happy to apply them.
4800W + 7350W = 12150W = 52.83A.
52.83 - 10 = 42.83A. 30% of 42.83A = 12.85A. Adding back in the 10A gives 22.85A design load, so well within the limits of 6.0mm2 and 32A breaker.
Add in another 5A if there's a socket combined with the isolator.
RE: the original gas hob. Left on as in heat causing danger (arguably safer than an electric one, since you can see a gas hob is 'on' from a distance) or the danger from escaping gas? Modern gas hobs should have flame failure devices that cut the gas supply after several seconds of no flame.
This is the layout. I took the back off the drawer unit and can get to the cable. Definite 6.00mm.
Dual oven to left, hob to right.
Can just cut the outgoing 6mm, and joint through with the cooker outlet plate.
Appliance delivery is on its way.
Edit.
Is the diversity calculation the same for 4 and 5 burners?
No mention of number of burners, or number of ovens either. The application of the diversity calculation as stated or not is ultimately the responsibility of the circuit designer of course. You wouldn't apply it to a commercial kitchen.
All up and running. Pulling roughly 6A per heating zone on the hob…. But it’s a really clever AEG ceramic hob and shuts off if there’s no pan on the zone.
Also AEG hood, and the two speak to each other. Turn on the hob, the hood lights up…. Any heat zone will turn on a fan, and the higher heat, the faster the fan.