Hi there.
Im new to calculating cable sizes and have got myself muddled up,please could someone help.
I am installing a radial for a new cooker 10.4kw and have an old wylex board with a spare 30a BS 3036 rewireable available.
I have worked out that with diversity that gives me 23a load,then factored in 30/0.725 for the fuse to give me 41.37a (In).
This will be run in mini trunking on its own over roughly 16 mtrs.
Looking in the reqs this is referene method B which would mean running the circuit in 10mm which seems excessive.
But as i said im new to this and am not sure if i am calculating right.
Any help would be really appreciated as i have spent far to long today driving myself mad with this
Thanks again in advance.
Im new to calculating cable sizes and have got myself muddled up,please could someone help.
I am installing a radial for a new cooker 10.4kw and have an old wylex board with a spare 30a BS 3036 rewireable available.
I have worked out that with diversity that gives me 23a load,then factored in 30/0.725 for the fuse to give me 41.37a (In).
This will be run in mini trunking on its own over roughly 16 mtrs.
Looking in the reqs this is referene method B which would mean running the circuit in 10mm which seems excessive.
But as i said im new to this and am not sure if i am calculating right.
Any help would be really appreciated as i have spent far to long today driving myself mad with this
Thanks again in advance.