Hi.
I am installing a new Hob and oven
the hob is induction 7.2kw
the double oven is 6.8kw and is to be hard wired

At the moment there is a 6mm 32amp supply for the hob
and a dedicated oven circuit on 2.5mm and 16 amp breaker

I have worked the oven with diversity to be just under 16amps.
I spoke to Neff who said it should be installed on a dedicated 20amp circuit.
without diversity it draws 29amps, could this cause a problem?
 
jujst change the 16A breaker for a 20A (assuming the 2.5mm cable's installation method allows for >20A and Zs complies for a 20A.
 
Hi. Thanks for your reply. That was my thinking. My main concern is that without diversity it draws over 29amps and if both were in use could this cause the circuit to trip? I have seen other ovens with lower power that say they require a 32amp circuit. Just thinking of the Christmas Day scenario when both are more likely to be used together. Thanks
 
yes, but with oven element/s on, the grill element would be off.an d if the manu. states a 20A circuit, then a 20A circuit is enough.
 
Last edited:

Reply to oven/ hob diversity in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
775
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
783

Similar threads

I believe the 6mm and 40A MCB debate is a little contentious at times. It depends on the installation method, being pretty close to the tabulated...
Replies
3
Views
357
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
907

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top