A

adam.h

Customer is having 2 ovens, both rated at 3K55W each so 15.5A

Would the best way be to run two 2.5 radials on a 20A mcb or have them on a 4mm ring 32A breaker (or rad even to seperate them?)

Also, they are having an induction hob rated at 7K09W, 31A. Would sticking this on a 32A mcb be cutting it a bit fine? otherwise it's 10mm instead of 6mm.
 
With the 2 ovens there is no reason not to put them on the same appropriately sized radial as long as they are both within 2 metres of the control switch.

With the induction hob i would consult the manufacturer just in case there is a power factor associated with it.
 
So it would be ok to have them both off the same control switch? Didnt think you could do that?

It's ok, have a look at the On Site Guide Appendix 8.4
"A circuit of rating exceeding 15A but not exceeding 50A may supply 2 or more cooking appliances..." goes on to say they must be in same room and within 2metres of the switch.:)
 

Reply to oven / induction hob question in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
Thank you, now the challenge is to get hold of 0.5m quickly 🤔
Replies
2
Views
2K
  • Question
Hi, we are replacing our old hob and cooker and I need a bit of help, to make sure all is safe. This is the oven and hob specs: AEG IKB64401FB...
Replies
0
Views
2K
  • Question
Thanks I have attached some photos just to see
Replies
17
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks