I'm fairly sure I'm on the right track here but would appreciate any thoughts...
Working on a kitchen re-furb whereby the old cooker was a free-standing range. The isolator was hidden behind the old units so a new 6mm radial supply has been provided with an above the worktop DP isolator / socket and 32A MCB. The load side of the supply has not yet been terminated to a ccu until the new cooker arrives. So far so good and all plastering and painting has been completed.
Units and appliances have arrived and the cooker has been changed...it is now a built-in oven unit with a gas hob. The oven 'instructions' are crap! The Chinglish label on the appliance states 230v and 2870 kW (!) assuming this is a typo that gives a max demand of 12.5A...there are NO recommendations regarding supply so at least I can't fail to comply with MI's! The supplied power cord seems to be about 1.5mm
Any fuse I fit obviously needs to be accessible and this unit is so deep there isn't room for a CCU behind it. There is no way further chasing / re-decorating will be entertained so another above the counter FSU is out of the question. I'm thinking of doing the connection in a JB behind the removable plinth. I think I could use 433.3.1 here and do away with overload protection, except for the 1.5 metre or so of terminal cable to the oven! but I also have a 16A mcb I could install in place of the 32A one, which would also protect the smaller cable.
As I see it by using the lower mcb I am affording SOME overload protection rather than rely on the 32A one and all protection & isolation devices are accessible. The connection below the units IS accessible for testing / inspection purposes.
As well as getting an answer I also get rid of the 60 day thing!
Working on a kitchen re-furb whereby the old cooker was a free-standing range. The isolator was hidden behind the old units so a new 6mm radial supply has been provided with an above the worktop DP isolator / socket and 32A MCB. The load side of the supply has not yet been terminated to a ccu until the new cooker arrives. So far so good and all plastering and painting has been completed.
Units and appliances have arrived and the cooker has been changed...it is now a built-in oven unit with a gas hob. The oven 'instructions' are crap! The Chinglish label on the appliance states 230v and 2870 kW (!) assuming this is a typo that gives a max demand of 12.5A...there are NO recommendations regarding supply so at least I can't fail to comply with MI's! The supplied power cord seems to be about 1.5mm
Any fuse I fit obviously needs to be accessible and this unit is so deep there isn't room for a CCU behind it. There is no way further chasing / re-decorating will be entertained so another above the counter FSU is out of the question. I'm thinking of doing the connection in a JB behind the removable plinth. I think I could use 433.3.1 here and do away with overload protection, except for the 1.5 metre or so of terminal cable to the oven! but I also have a 16A mcb I could install in place of the 32A one, which would also protect the smaller cable.
As I see it by using the lower mcb I am affording SOME overload protection rather than rely on the 32A one and all protection & isolation devices are accessible. The connection below the units IS accessible for testing / inspection purposes.
As well as getting an answer I also get rid of the 60 day thing!