My parents are having a new kitchen installed soon and had someone out today to check over the room before they make their final decisions.

My mum wants a double electric oven and induction hob, but the kitchen fitter has said that the cable installed (which is completely hidden and inaccessible!) isn't sufficient and that they'll be needing a new circuit run, which will require a new consumer unit as there is no space available in the existing one.

I'm very suspicious of this conclusion as the current (un-used) cooker circuit is in 6mm and protected by 40A MCB. Besides, this forum has taught me not to trust the electrical abilities of kitchen fitters.

Decided to do the calculations (diversity etc) for their new cooking set-up myself, but ran into a problem... none of the manufacturers seem to mention the maximum current draw of their appliances...

Anyone know why this is? What figures should I be using?
 
What do you mean by "completely hidden and inaccessible"? 6mm cable shouldn't really be protected by a 40amp MCB in the first place so I would upgrade this to 10mm if possible then any oven/hob combo would be covered.
 
....none of the manufacturers seem to mention the maximum current draw of their appliances...

I can't believe that any of these appliances haven't got a Power (Watts) rating on them somewhere...a label or instructions
 
Last edited by a moderator:
Ok I will have a stab first a bit of history when electric cookers came out it was just that an electric cooker with hob and oven combined so 6 mm and a 30 amp fuse at the time was suffice ok.

Now years later they split the hob and the oven now you could connect both to the 6mm circuit and if you have read a previous post on the subject you will see the thoughts on connecting them and that fine So whats the problem now well now there are double ovens and induction hobs the double oven can now take the load of an old combined cooker hence why the guy who has surveyed it has calculated that the supply cable either has to be uprated or he has to run another 6mm circuit and have the oven on one and the hob on the other.

One thing to be aware of Christmas day ?????? you say well some houses have a 60 amp main fuse but people want bigger and better so double ovens 10Kw showers , immersion and daughter blowdrying her hair and bingo you could blow the main fuse when all 3 are going at the same time plus this does not include any other equipment that is on at the same time.
 
Last edited by a moderator:
Thanks for the help.

My parents haven't picked an oven or hob yet, I'm just practicing a few calcs and checking the kitchen fitters work!

Just curious about the diversity calcs now. According to 17th I can say that the circuit will be rated at 10A + 30% of the remainder (+5A for a socket, but this doesn't matter in my case). So a 6mm T+E would be compliant in most cases, but just bad practice? Am I getting the right idea?
 
If a 6mm cable complies/is compliant with your calculated loading, ...How can you then call it bad practice?? ...So NO your not getting the ''right'' idea!!

Please look at the numerous other threads on this subject at the bottom of this page....
 
Not sure I follow... 6mm is good for 47A at ambient temperature.

Ok, so 47 amps at ambient temperature clipped direct. No problem there. Now look at method 100, above a plasterboard ceiling covered by insulation not exceeding 100mm... 34 amps. Then add some voltdrop for good measure and any other factors and you can see why 6mm is normally protected by a 30/32 amp device.

If you are telling me that this cable is within a few feet of the CU, does not pass through any insulation at all and has no other derating factors, then I stand corrected. :smile5:
 
Last edited:
I wondered if that was what you were getting at, fair point.

Although in this case, you stand corrected I'm afraid! :wink5:

Consumer unit is in the kitchen and the run to the cooker will be about 10 feet, embedded in or clipped to plaster.

Another quick question about the diversity calculations.

Will the total load be:

10A + 30% of remainder (hob + oven)

or

10A + remainder of hob + 10A + remainder of oven

Cheers!
 
Thanks for the advice. Having looked at the consumer unit myself, I've found an unused way (used to be for bell transformer) so if I can get the a new MCB then that will be used for one of the appliances.

Done the calculations anyway for practice. Does someone mind checking my maths? pleeeease!

Induction hob: 7.2kW = 31A

Oven: 4.5kW = 19.5A

Total without diversity = 50.5A


Diversity

Hob: 10A + 21 x 30% = 16.3A

Oven: 10A + 9.5 x 30% = 12.85A

Total = 29.15A


Cable installed: 6mm, 8m run, ref method C, ambient temperature

Voltage drop = 1.8v

Protective device - 40A Type 2 (max Zs for 5 sec disconnect = 0.66 ohm)

(R1+R2) per metre = 10.49mohms

Zs = 0.01049 x 8 + 0.35 = 0.43 ohms - compliant


Hope this makes sense, just basically typed up my handwritten notes from earlier.

Does it all look ok?
 
The only thing i would add is diversity is not an exact science and the use of the appliance can still be a major factor. Sure when ervything is up to temp and the heaters are coming in and out under thermostat control you can see diversity working for you. BUT if the user fires up all rings and oven elements from cold (unlikely i know) but quite possible then you are looking at full load against the rating plates.
No biggy but worth keeping in mind
 
The only thing i would add is diversity is not an exact science and the use of the appliance can still be a major factor. Sure when ervything is up to temp and the heaters are coming in and out under thermostat control you can see diversity working for you. BUT if the user fires up all rings and oven elements from cold (unlikely i know) but quite possible then you are looking at full load against the rating plates.
No biggy but worth keeping in mind

And the phone call christmas day...

"Hi you fitted my oven and hob back in March, I'm in the middle of cooking my Christmas dinner and they've both stopped working!! You need to come and fix it for me!! Please?"
 
Would 30% additional capacity (40A MCB) on top of the diversity calculation is reasonable in case of big xmas dinners etc, especially as the 6mm is rated at nearly double the calculated total anyway?

Wouldn't the oven and hob have to be running full belt for a considerable time for the MCB to trip anyway? Been trying to find the graph in the BGB of time versus current but can't seem to see it...
 
There is usually a big ring on the hob that takes loads of juice, instead of struggling with diversity just tell her what combination to use, i.e. If both ovens are on don't fire up the big hob ring or something like that.
Otherwise either put two supplies in (preferable) or a real big one.

Happy Xmas
 
Right o here is my 2 p worth.a double oven usually a oven and grill will draw usually 20-26A with both of them on.an induction hob with 2zones on boost will draw 36-40A.thats everything from baumatic to gaggenau that I've fitted and everything inbetween.ive had 5zone Miele ceramic Hobs rated t 8.5kw that I couldn't get above 20A with all rings on full blast.point is I find the induction a slightly different beast in terms of diversity and usually put it on its own circuit whenever possible.as previous posts allow for the Xmas day test if poss
 
If the stove circuit is easy to replace being so close to the CU then maybe just get the ovens and the induction hob installed and do a real life test to see the load characteristics. If the circuit turns out to be inadequate then replace it, if not you've saved some money.
 
Similar situation when we did our kitchen at home. 900mm Induction Hob and double oven. I ran a 10mm protected by a 40A MCB for the Hob and 6mm protected by a 32A MCB for the oven just to be safe. And if you have never had an Induction Hob before...they are bloody brilliant.
 
an induction hob with 2zones on boost will draw 36-40A.thats everything from baumatic to gaggenau that I've fitted and everything inbetween.ive had 5zone Miele ceramic Hobs rated t 8.5kw that I couldn't get above 20A with all rings on full blast.

Is this because Induction Hobs use magnetic fields or something and dont actually 'Heat' up whereas standard Hobs use Heat to Heat the pans?
 
Conventional and ceramic Hobs click on and off with the stats and the induction Hobs reduce the load to the zones the further you turn them down(i think!)whack a zone on boost and the electro mag bit revs it's nuts off exciting all they electrons turn it down to 5 or 6 and it just simmers away
 
And the phone call Christmas day...

"Hi you fitted my oven and hob back in March, I'm in the middle of cooking my Christmas dinner and they've both stopped working!! You need to come and fix it for me!! Please?"

I wonder how many of us have had this Christmas day phone call when designing cooker circuits using diversity?

Its not just Christmas day that cookers are fired up to the hilt, i bet there's plenty of families who have a full monty Sunday dinner almost every week.
 
Similar situation when we did our kitchen at home. 900mm Induction Hob and double oven. I ran a 10mm protected by a 40A MCB for the Hob and 6mm protected by a 32A MCB for the oven just to be safe. And if you have never had an Induction Hob before...they are bloody brilliant.

We have a 7.6KW induction hob and a standard single multi element oven. Both run originally off 6mm singles on a 30A type 2 MCB (Now a 32A type B RCBO) Never had a single problem with this set-up in the 2 years or so the induction hob has been installed... So why you think you need a 10mm and 6mm cable supply to your set up is beyond me!!! lol!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Ovens and hobs - why no tech specs provided?!
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
DNS1,
Last reply from
Engineer54,
Replies
26
Views
4,384

Advert

Back
Top