B

blue eyes

hi all

I have a 3phase compressor to wire. there is a spare 3phase way available 20A.
The compressor in ratedat 10A. Now I an of the feeling that the MCB is to protect the cable which will be 2.5mm swa (and not the compressor which should have itown mean of protection)


this is a commercial property with type C breakers But I have searched all local wholesalers and the MCB are so old I can not get one.


The compressor is to beplaced inside a metal storage cabin which has power light supplied bya T.T supply.
I am a bit concernedthet there may be a problem in introducing a compressor supplied by aTN-C-S supply

cheers Blue eyes
 
Last edited by a moderator:
Overload, as in motor protection overload relay!

You haven't told us the size of the motor so how is anyone supposed to help!

As for TT have you even thought how compressed air is piped?
 
hi all

I have a 3phase compressor to wire. there is a spare 3phase way available 20A.
The compressor in ratedat 10A. Now I an of the feeling that the MCB is to protect the cable which will be 2.5mm swa (and not the compressor which should have itown mean of protection) Yes the MCB is to protect the cable, the compressor if over 0.37kw will have an overload built into it's control system.


this is a commercial property with type C breakers But I have searched all local wholesalers and the MCB are so old I can not get one. Then you need to design a different approach to this then


The compressor is to beplaced inside a metal storage cabin which has power light supplied bya T.T supply.
I am a bit concernedthet there may be a problem in introducing a compressor supplied by aTN-C-S supply There are several options here available but it depends on enviroment, such as is the site Agricultural etc.
Why was the cabin made TT?
Where does the supply for the cabin lights come from?
You could tie the TT rod to the TNC-S system if allowed. You could make your supply to the compressor a sub main, protecting the sub main by TNC-S and then divorce it from the TT system and have the compressor on TT.
Really need more info

cheers Blue eyes

.........................
 

Reply to over current protection to compressor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
710
My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top