Hi all I'm after some views on a job I'm pricing, pme 3 phase 3x100amp fuse holders supplying a fair size commercial unit, which was split into two units. Small unit is basic lights and sockets with few wall heaters (3 phase d.b)., main unit is a gym in which he is wanting to add two more beauty rooms and two 3 phase sunbeds. Now one is on 20 amp MCB and the other a 32 amp . the gym has four electric showers at 8.5 kW .
The small unit is open daytime only, I've clamped the tails when the small unit is open and with the gym lighting on and a few treadmills I saw 40 amp on one phase 10 on another and 3 on the last, so its not well balanced at all.
With the small unit shut I clamped the tails again with just the gym running and I turned all showers on etc and the external lighting , I saw 50 amps on one phase and 40 each on the other two. My concern is that its warmish at the mo and there's no electric heating in use or any air con so this lot plus the two sunbeds ( no more info at the moment on them except what MCB size) plus hair dryers and other bits is going to be pushing its luck and if its daytime and the small units open thats an issue. I know the sunbeds will have a higher inrush when turned on and then settle down but I still reckon they will pull prob 15 amp per phase for the smaller one and 24 ish for the bigger one and they'll be on n off a lot.
I'm not sure if the supply fuses are actually 100 amps or could be 80 amps. I've thought about losing two of the showers but they get used a lot and this could be a customer issue. I don't see there's that much diversity to play with either as all lights are constantly on etc. Maybe some with the showers but these are steadily used at all times.
Am I been sensible or over cautious ???
Regards
Pete.
The small unit is open daytime only, I've clamped the tails when the small unit is open and with the gym lighting on and a few treadmills I saw 40 amp on one phase 10 on another and 3 on the last, so its not well balanced at all.
With the small unit shut I clamped the tails again with just the gym running and I turned all showers on etc and the external lighting , I saw 50 amps on one phase and 40 each on the other two. My concern is that its warmish at the mo and there's no electric heating in use or any air con so this lot plus the two sunbeds ( no more info at the moment on them except what MCB size) plus hair dryers and other bits is going to be pushing its luck and if its daytime and the small units open thats an issue. I know the sunbeds will have a higher inrush when turned on and then settle down but I still reckon they will pull prob 15 amp per phase for the smaller one and 24 ish for the bigger one and they'll be on n off a lot.
I'm not sure if the supply fuses are actually 100 amps or could be 80 amps. I've thought about losing two of the showers but they get used a lot and this could be a customer issue. I don't see there's that much diversity to play with either as all lights are constantly on etc. Maybe some with the showers but these are steadily used at all times.
Am I been sensible or over cautious ???
Regards
Pete.