So customer reporting she plugged in a faulty LED light and it tripped both upstairs and downstairs lighting MCBs indicating that the circuits are connected (the board has no RCDs - yet). Before I go and do a CU change to RCBOs I need to identify the source of this fault. I'm interested to hear how others might approach this scenario in terms of the fault-finding method? Is it just a case of testing continuity between MCB 1 and the fixtures of circuit 2 until you find a leg that shows a connection is present?
 
After checking the appliance that was plugged in, an electrician would use their MFT and go through all the testing sequence's to identify what/where the fault was, if any.
 
If there is some cross-connection of circuits, likeliest place is a light with switches present both upstairs and downstairs. Typically this means the landing light (e.g. borrowed N, or accidental cross-connection at hall or landing 2-gang switch).

Switch everything on, then disconnect cables at the CU and test between L of one and N of the other.
 
You might start off with a global insulation test, and if any problems work down to individual circuit insulation tests. You also need to ensure there are no borrowed neutrals or interconnecting circuits. As already said in #2, go through all testing sequences, loose connections may also contribute.
 
It is worrying as it implies they are linked. Cross-coupled rings is one of the C2s mentioned in the BPG#4 but it takes a bit more 'bad effort' to link other types of circuit!

Approach fault-finding with logic and care, in particular you should never assume it has been done properly! So usual of IR testing but also see if the circuits have linked L or borrowed N, and be aware it might only happen for certain light switch position combinations!
 
The OP is going to be changing a CU to all RCBO's but does not know how to find a fault on a lighting circuit, am I the only person that finds that a bit strange, I wonder who will be issuing the notifications.
think it's more that OP is seeking other ideas as forearmed is forewarned. we all know the situation with landing lights 2 way switching (L from 1 circuit, N from another) but there's also diy dave'sinput with his sticky paws where they should keep away.
 
think it's more that OP is seeking other ideas as forearmed is forewarned. we all know the situation with landing lights 2 way switching (L from 1 circuit, N from another) but there's also diy dave'sinput with his sticky paws where they should keep away.
That's the nub of the matter I am alluding too, if the question had been asked after going to the premises and not finding the fault that would make sense, but the original question/hypothesis was "is it just testing continuity" it rang alarm bells for me.
 
If any circuits are interconnected in a way that causes two single-pole* MCBs to trip on a single fault, the fact that the circuits are interconnected at least on the line side will be immediately obvious, because both will need to be turned off before the circuit goes off.

*Not relevant here, but I qualified this with 'single pole' because with DP MCBs, a short circuit at a point with a borrowed neutral could cause the same symptom. One breaker sees the fault current on the line and the other on the neutral and hence both trip.
 
It's also rare but possible that the lighting was originally wired as a ring then at the first CU upgrade some bright spark decided to put the 2 cables into seperate MCBs without any testing.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Overcurrent fault tripped two MCBs
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
JosephandAmber,
Last reply from
Dave OCD,
Replies
15
Views
2,565

Advert

Back
Top