Overhead SWA Supply | on ElectriciansForums
Discuss Overhead SWA Supply in the UK Electrical Forum area at ElectriciansForums.net
R
Richard
Good afternoon, Hope everyones well!
Quick question.
Running a 60A sub-main top adjacent barn about 40 odd meters away. I'd naturally prefer burying the cable however the client would rather overhead. I'v only ever suspended T+E cable on a catenary set-up. Is there any reason an SWA can't be run in this fashion? Obviously there'll be poles at intervals because of the span and weight, but i'm thinking in long term wear/movement damage to the cable.
Thank you for any advice.
Id be inclined to use a flexible cable in preference to SWA if it's possible.
One cable you certainly should not be installing on an outdoor catenary is T&E.
When designing the catenary you will need to work out the tension that will be put on the fixings and the amount of sag which needs to be allowed in the wire.
  • [ElectriciansForums.net] Overhead SWA Supply
Quick question.
Go back to the suspended T&E and change it for a more appropriate cable?
whats wrong with swa? you can get it with catenary wire incorporated in the cable
Thank you for your reply.
I'v personally never recalled seeing much guidance on this. Is there any guidance readily available?
The cable manufacturers data sheet will give you the mass/metre of the cable, similarly the mass/metre of the catenary can be obtained.
Then you use the physics you learned at school to calculate the tension on the catenary and forces exerted on the fixings.
You can select suitable fixing using this information, but also taking in to account the strength of whatever you are fixing in to.
I have seen the whole top corner of a house ripped away by a DNO overhead when a tree hit the cable!
Reply to Overhead SWA Supply in the UK Electrical Forum area at ElectriciansForums.net
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.