Question an under floor heating/ cooling box reading 17amp on my clamp meter but the supply is from a 13amp plug now I no a fuse or mcb can take 1 1/2 times its load for a certain time not sure for how long but my question is why hasn't this took the 13amp fuse out
 
Question an under floor heating/ cooling box reading 17amp on my clamp meter but the supply is from a 13amp plug now I no a fuse or mcb can take 1 1/2 times its load for a certain time not sure for how long but my question is why hasn't this took the 13amp fuse out

Have a look at the time/current characteristics (appendix 3 in BS7671). I cant find any tables for a BS1363 fuse that you are looking for but to put it in perspective a 15A BS3036 fuse will take 5 minutes to blow with 30A running through it and would take days of continuous use (probably weeks... if at all) to blow with 20A running through it, so I cant see 17A troubling a 13A fuse too much. At a guess I would say a week of continuous use at 17A might blow it, but a few hours a day probably wont touch it!
 
Last edited:
Have a look at the time/current characteristics (appendix 3 in BS7671). I cant find any tables for a BS1363 fuse that you are looking for but to put it in perspective a 15A BS3036 fuse will take 5 minutes to blow with 30A running through it and would take days of continuous use (probably weeks... if at all) to blow with 20A running through it, so I cant see 17A troubling a 13A fuse too much. At a guess I would say a week of continuous use at 17A might blow it, but a few hours a day probably wont touch it!


BS1362 fuse.
 

Reply to Overload in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
786
  • Question
Interesting what you say, I have allowed with my system for the change to be half hour out, so start charging at 0:30 and stop at 7:30 but night...
Replies
1
Views
795

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top