I had to investigate the reason for an mcb tripping, this mcb was suppling a small outside tea shed. After investigation I found that the tea shed was protected by an 20amp mcb, with a clamp meter I measured the circuit was pulling 37amps but was not tripping. It seemed to trip after about 6 minutes. I was wondering if this is something someone has come across before and explainable in the regs book.
 
I had to investigate the reason for an mcb tripping, this mcb was suppling a small outside tea shed. After investigation I found that the tea shed was protected by an 20amp mcb, with a clamp meter I measured the circuit was pulling 37amps but was not tripping. It seemed to trip after about 6 minutes. I was wondering if this is something someone has come across before and explainable in the regs book.


Overload currents occur in circuits which have no faults but are carrying a higher current than the design value due to overloaded machines, an error in the assessment of diversity, and so on. When a conductor system carries more current than its design value, there is a danger of the conductors, and hence the insulation, reaching temperatures which will reduce the useful life of the system.
The devices used to detect such overloads, and to break the circuit for protection against them, fall into three main categories:
1. -Semi-enclosed (rewirable) fuses to BS 3036 and cartridge fuses for use in plugs to BS 1362.
2. -High breaking capacity (HBC) fuses to BS 88 and BS 1361. These fuses are still often known as high rupturing capacity (HRC) types.
3. -Circuit breakers, miniature and moulded case types to BS EN 60898.
Examination of the characteristics of these devices indicates that they are not the 'instant protectors' they are widely assumed to be. For example, an overloaded 30 A semi-enclosed fuse takes about 100 s to 'blow' when carrying twice its rated current. If it carries 450 A in the event of a fault (fifteen times rated current), it takes about 0.1 s to operate, or five complete cycles of a 50 Hz supply.
HBC fuses are faster in operation, but BS 88 Part 2 specifies that a fuse rated at 63 A or less must NOT operate within one hour when carrying a current 20% greater than its rating. For higher rated fuses, operation must not be within four hours at the same percentage overload. The latter are only required to operate within four hours when carrying 60% more current than their rated value.
Circuit breakers are slower in operation than is generally believed. For example, BS EN 60898 only requires a 30 A miniature circuit breaker to operate within one hour when carrying a current of 40 A. At very high currents operation is described by the BS as 'instantaneous' which is actually within 0.01 seconds.
All protective devices, then, will carry overload currents for significant times without opening. The designer must take this fact into account in his calculations. The circuit must be designed to prevent, as far as possible, the presence of comparatively small overloads of long duration.
The overload provisions of the Regulations are met if the setting of the device:
1. -exceeds the circuit design current
2. -does NOT exceed the rating of the smallest cable protected
In addition, the current for operation must not be greater than 1.45 times the rating of the smallest cable protected.
There are some circuits which have widely varying loads, and it would be unfortunate if the protection operated due to a severe but short-lived overload. In such cases, the heating effect of the currents must be taken into account so that the overload setting is based on the thermal loading.
 

Reply to Overloaded MCB not tripping. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top