You know I havent actually noticed the cable size for the supply but its an armour supplying it! And from what i can remember it cant be bigger than 4mm!
 
If 4mm cable then you certainly haven't got a 63amp supply , 32amp max.
wots the size of the mcb or fuse suppling the extension submains ?
 
Haven't dug that far yet, but as soon as you asked about what was supplying it I was in the regs book... The futher this conversation goes on the more dodgy this is looking!
 
What have you actually looked at? I’m sorry but this is the third question you’ve asked today, all about the same job. One oven became two, you feed dribs and drabs of information but your not sure on the information you do give.

This is developing in to pure fantasy.
 
I saw this posted somewhere as another method of working out maximum demand/diversity and this would bring me within the maximum demand if it weren't for biff pointing out the fact the 64A board is supplied with a 4mm cable so it won't actually be 64A, will be going top check out what size of breaker is supplying the board later
 
Diversity calcs are just a guess, the regs give you something to work with but reality will be different. With that type of load you will need to look at the end to end installation from Cu main all the way to appliances. As mention it stuff starts to trip or burn out, i am pretty sure you will be back at your expense and pointing the regs book at the client wont help.
Having said that rating plates are maximums and are rarely encountered and if they are it is for a short duration. This is where experience comes in.
 
Do yourself a favour pal and walk away.
Find other domestic work to gain experience from as i've a feeling that the customer isnt going to pay to have the job done properly.
The fact that the sparks who put the submains in originally have'nt come back to do the alterations is all the answer i need.
 
At long last a sensible suggestion.
The original installer didn’t know what he was doing, neither does our OP.

2 ovens
Induction hob
Ring main
Etc

One 6mm feed, it’s not going to work which ever way you look at it.
 
Is this a commercial premises or a domestic one? What's the chance they're going to use 2 ovens plus a hob simultaneously? Sometimes a thick coat of common sense can be as good if not better than a diversity calculation.

you,ve never seen me cook then lol
 

Reply to overloading the board? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top