Any of you ever come across overloads protective devices failing? Was testing a installation yesterday with water pumps and the pumps were wired in 1.5 HO7 RNF on a 40 Amp BS88-2 however the start and run windings of the pump motor were both protected by 6Amp overloads.
 
Anything can fail. Overload relay protects the device, not the wiring, so 40A is a bit too high in my opinion.
 
Agreed. The high rating of the fuses has been used only for fault protection so that a small disconnection time is achieved. As the pumps were drawing such a small current I recorded it as a C2 with further investigation required.
 
Any of you ever come across overloads protective devices failing? Was testing a installation yesterday with water pumps and the pumps were wired in 1.5 HO7 RNF on a 40 Amp BS88-2 however the start and run windings of the pump motor were both protected by 6Amp overloads.
Tried to red your avitar , what does it say lol?
 
however the start and run windings of the pump motor were both protected by 6Amp overloads.
If you mean there was an overload for each winding I've never seen an arrangement like that. Usually the same overload would protect both windings. It is possible for overload relays to fail, short circuit damage and even insects inside them could cause it.

The 40A fuse with the 1.5mm cable is oversized even for neoprene I might suggest 20A would be more suitable.
 
Sorry marvo you are correct one overload for both sets of conductors for both windings!What a difference an 's' makes. It's just that it would be a pretty bad scenario that if the overload were to fail and the contactor was to be welded shut, if the pump were to pull a greater current because of a rag stuck in its motor, then the conductors are left under rated. Personally I would recommend the 20A as well to achieve suitable fault current protection.
 

Reply to Overloads in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
818

Similar threads

He only posted the one message then never came back.
Replies
2
Views
828
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top