Can anyone help since the summer is coming when my solar started to rise is seems that I am using more eletric , I.e solar at 3.70 kW and my energy used is around the same can anyone help
 
Yes I have done that , I have taken the clip off the eletric box and I am still getting a reading

Hi Twindecks. The most likely issue is that the CT clamp on the supply live tail needs to be flipped over so that it faces the other way around.

One of the two clamps measuring solar generation should be linked to the CT clamp on your supply live using a "Y" cable.

The CT clamp that is on the supply live must face in the opposite direction to the CT clamp on the the PV live otherwise the device adds the generation to the amount used from the grid rather than taking it away.

It is generally easier to access the CT clip on the supply live rather than on the PV live hence my suggestion.

All you need to do unclip the CT clamp, turn it 180 degrees and then clip it back on.

I hope this helps.

Andrew
 

Reply to owl Pv intuition in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

We’ve recently completed the first and second fix of a barn conversion that is off grid with solar PV, batteries and a back up generator. This...
Replies
0
Views
280
Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
930

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top