Discuss p.f.c in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S

s.keech

hi have started to do some testing but I am stuck on p.f.c and p.s.c.c test. have looked at gn3 and that is not clear with no illustrations and brian scadden book and also kitcher youtube video. Has the main switch got to be off for both of these tests and test on incoming L-N for p.s.c.c and L-E for p.f.c also should the main earth be connected as I know it should not be for ze. Thanks for any help.
 
main switch off. test as you say with earthing and bonding connected. if it's PME then pscc and pefc will be the same.
 
IN a nut shell your exactly right mate, do your ze then re connect your main earth and do your pscc and pfc. Highest value of the both is recorded
 
test on incoming L-N for p.s.c.c and L-E for p.f.c

In principle that's right but it may be worth checking the relevant bit of the manual for your tester. On mine, regardless of which of the two tests you're doing, it says put L probe to L, N probe to N and E probe to E. Then select either loop or line test mode on the functions dial and test.
 
In principle that's right but it may be worth checking the relevant bit of the manual for your tester. On mine, regardless of which of the two tests you're doing, it says put L probe to L, N probe to N and E probe to E. Then select either loop or line test mode on the functions dial and test.

is that a fluke? with the megger, it's a 2 lead job for Ze and pfc testing.
 
main switch off. test as you say with earthing and bonding connected. if it's PME then pscc and pefc will be the same.

There are 3 good reasons for doing it this way.

Firstly it is the correct method as Tel says.

Secondly you want the worse case scenario of Ze, i.e highest impedance on the supply to ensure your test result is that of the supply only, so no parallel paths.

Thirdly, you want the worse case scenario again, and the highest current measurement as possible PEFC/PSCC, so if your bonding and CPCs are not connected, then the result will be lower due to the lack of parallel paths, and so could lead to having unsuitably rated protective devices.

Cheers.............Howard
 
eh? I haven't heard of this before, I was taught for three phase you measure PSCC phase - phase.

Maybe that's what you do if you've got a meter that can do it, but if you don't it's acceptable to double worst-case single phase PFC (which is the method I was taught)?
 
what he means is if your mft will not measure phase-phase, then measure phase-N and double the value ( should actually be x 1.732 ).
 

Reply to p.f.c in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
617
  • Question
I think the point made here on knowing the calculations for verification of results etc is a good one. With one question leading onto the next not...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top