We have a 5pair cable which is overall screened. This cable takes 3 alarm signals from a panel to the DCS, 2 pairs are spare. Does the screen have to be earthed at one side only? And can the screen be left unearthed?
thanks
thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Paired cable screens in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
We have a 5pair cable which is overall screened. This cable takes 3 alarm signals from a panel to the DCS, 2 pairs are spare. Does the screen have to be earthed at one side only? And can the screen be left unearthed?
thanks
What are you doing with spare pairs? It's not unusual to take them to protective earth, especially in an ATEX install.
I would also expect to see a separate instrument earth at the DCS, and from there, a screen earth bar.